How exactly do you go about sizing the Shear Connector(stud) for the connection of concrete facing wall to a steel soldier pile? I have assumed it's based on the horizontal shear stress created by the soil load on the concrete wall, treating the conc like a simply supported slab, but the results I get are making me rethink.
I have calculated a Max Shear on the facing of about 11 kips at the support end (pile location) based on a uniform load of 1.4k/ft(soil pressure at bottom of 30' wall), 10' span and 1.6 load factor. Then, using Shear = VQ/I I get 1.4k/in. So, considering a 12" section of the wall, I get 17 k of horizontal shear force. That would require me to use 5/8"dia studs at 6" (9kip/stud) but that seems awfully high.
Am I missing something or just being WAY to conservative?
I have calculated a Max Shear on the facing of about 11 kips at the support end (pile location) based on a uniform load of 1.4k/ft(soil pressure at bottom of 30' wall), 10' span and 1.6 load factor. Then, using Shear = VQ/I I get 1.4k/in. So, considering a 12" section of the wall, I get 17 k of horizontal shear force. That would require me to use 5/8"dia studs at 6" (9kip/stud) but that seems awfully high.
Am I missing something or just being WAY to conservative?