jbjones2001
Structural
- Sep 19, 2002
- 14
I have a question in modeling concrete shear walls configured in a tube, like that found around a stair or elevator. My question is related to a possible difference in how the building should be modeled to calculate drift, and how it should be modeled to design the walls to ACI.
ACI chapter 21, limits the effective flange width of a shear wall to 1/4 the wall height. If I use this criteria the "flange" of the tube is not fully effective, thus the structure should not be modeled as a tube, but two "C" shaped sections.
The question arises in that Two "C" shaped sections potentiall have far less moment of interia than the tube section, depending on how much of the tube flange is effective in the "C's".
So should the building be modeled assuming tube behavior, or "flanged" behavior for calculating drift?
It appears evident by ACI that it should be modeled using "flanged" behavior.
ACI chapter 21, limits the effective flange width of a shear wall to 1/4 the wall height. If I use this criteria the "flange" of the tube is not fully effective, thus the structure should not be modeled as a tube, but two "C" shaped sections.
The question arises in that Two "C" shaped sections potentiall have far less moment of interia than the tube section, depending on how much of the tube flange is effective in the "C's".
So should the building be modeled assuming tube behavior, or "flanged" behavior for calculating drift?
It appears evident by ACI that it should be modeled using "flanged" behavior.