Shear Friction Reinforcement VS. Max Steel Area

Status
Not open for further replies.

blawson

Structural
May 9, 2006
3
Does reinforcing area used for Shear Friction according to ACI 318 section 11.7 count towards the maximum steel percentage for 0.75pb?
 
Replies continue below

Recommended for you

You can count for longitudinal steel to account for Shear friction. As long as there is no net tension on the section, the longitudinal steel that is used for flexure can also be used for shear friction.

See commentary for 11.7.7 (ACI 318-05)
When moment acts on a shear plane, the flexural tension stresses and flexural compression stresses are in equilibrium. There is no change in the resultant compression Avf fy acting across the shear plane and the shear-transfer strength is not changed. It is therefore not necessary to provide additional reinforcement to resist the flexural tension stresses, unless the required flexural tension reinforcement exceeds the amount of shear-transfer reinforcement provided in the flexural tension zone. This has been demonstrated experimentally.

 
So if I have a bending moment around a corner of a wall that req's As = 0.31 sq.in. of steel, and the shear values exceed the allowable Vc and I need to use Shear Friction, do I not have to "add" additional steel? If Avf = Vu/(phi*Fy*mu) = 0.09, do I not have to use 0.40 sq.in of reinforcing?
 
Concerning developing a corner moment, refer also to the following:
thread507-228698
 
blawson,
Can you expand a bit on your wall corner example? Usually the reinforcement used for bending is orthogonal to the shear reinforcement in a bending member since the shear cracks are usually at an inclined angle to the flexural "beam" and thus the shear reinforcement is not aligned with the flexural. Thus there is no conflict.

 
Shear reinforcement for out of plane bending in walls is not a common thing, and normally indicates the walls are too thin.
 
You can't use shear friction reinforcement to make up for a deficiency in shear capacity of the concrete. As JAE mentioned, you use stirrups for that.

But I wouldn't use stirrups in a wall--I would thicken the wall as hokie66 suggested.

DaveAtkins
 
Just to point this out, too. You can only use shear friction
in certain circumstances. You need to have a
cold joint or a reasonable expectation that a crack will occur along the plane in question - a SHEAR plane. Diagonal tension cracking doesn't count as a shear plane.
 