Hi there,
I've been looking around for information about this topic, but can't seem to find much. The problem I'm currently having is that I'm verifying the capacity of an existing concrete structure to see if it can be used for storage (7.2 kPa, 150 psf), and many provisions regarding shear induced tension were not in place when the building was built. As such, nothing in 11.3.9 in the A23.3-04 standard is satisfied at the supports, mostly because the bottom steel isn't properly developed.
In clause 11.3.9.5 it says that in the formula (Vf - 0.5Vs - Vp) * cot (theta), Vs cannot be higher than Vf. However, I've been told that the Vs that should be used in the formula is the portion that the steel will resist - or rather the portion that the concrete cannot resist - and should be calculated as Vs = Vf - Vc.
Can I really use Vs = Vf? Any input on this topic would be greatly appreciated.
Thank you for your time.
I've been looking around for information about this topic, but can't seem to find much. The problem I'm currently having is that I'm verifying the capacity of an existing concrete structure to see if it can be used for storage (7.2 kPa, 150 psf), and many provisions regarding shear induced tension were not in place when the building was built. As such, nothing in 11.3.9 in the A23.3-04 standard is satisfied at the supports, mostly because the bottom steel isn't properly developed.
In clause 11.3.9.5 it says that in the formula (Vf - 0.5Vs - Vp) * cot (theta), Vs cannot be higher than Vf. However, I've been told that the Vs that should be used in the formula is the portion that the steel will resist - or rather the portion that the concrete cannot resist - and should be calculated as Vs = Vf - Vc.
Can I really use Vs = Vf? Any input on this topic would be greatly appreciated.