Shear strength acc. ACI 318R-02

Status
Not open for further replies.

bender36

Structural
Mar 5, 2007
12
Hi,

the shear strength provided by concret Vc is given in clause 11.3.1.1. The version which I have says:

Vc=2*(sqrt(fc')/6*bw*d

in the internet I found:

Vc=sqrt(fc')/6*bw*d, but realted to the same code release.

Same appwears for the limit of Vs (clause 11.5.6.9):

Vs=8*sqrt(fc')*bw*d

and

Vs=2/3*sqrt(fc')*bw*d

WHAT IS CORRECT ?

Thank you very much,

Martin
 
Replies continue below

Recommended for you

Upgrade to the latest edition and go metric. ACI 318M-05.
 
I'm not sure where you get the /6 in the Vc formula.

ACI 11.3.1.1, Equation 11-3 shows:

Vc = 2([√]f'c)bwd

The value in section 11.5.6.9:

Vs = 8([√]f'c)bwd
is a maximum limit on your steel shear reinforcing contribution.

I don't see where there is a Vs = 2/3([√]f'c)bwd

Vc and Vs are two different things.

 
bender35,

When you use a new formula that you are no sure about, check it to make sure it makes sense. In your case a higher area would have resulted in a lower shear capacity - obviously something was wrong.

It doesnt work so well on this formula, but usually putting the units into the formula should give you the correct units as a result (i.e kips/lbs for a force or psi for a stress).
 
Check in ACI 318-05 (SI units), you will find:
11.3.1.1, Equation 11-3
Vc = 0.17(?f'c)bwd
11.5.7.9:
Vs = 0.66(?f'c)bwd
 
the first you mention for Vc and Vs are in imperial units, the second are in Metric units
 