Shear strength of embedded anchor bolts in CMU

Status
Not open for further replies.

EBF

Structural
Jun 2, 2003
62
0
0
US
If I have anchor bolts embedded in a CMU wall (f'm=1500psi)that is fully grouted (grout f'c=4000psi), is it ok to use the shear strength values from 1997 UBC Table 19-D for bolts embedded in concrete, rather than the values listed in Table 21-E for bolts embedded in masonry? Or do the values for masonry already take into account fully grouted units with higher strength grout?
 
Replies continue below

Recommended for you

I think your problems can be best answered by a question also.

Who’s holding the grout?

I will use the values listed in bolts embedded in masonry, even if it is 1,000,000psi grout (just exaggerating).

For your second question, my answer is “ perhaps they already consider a certain strength of grout but maybe not higher “.

Many thanks.
 