Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Shear Wall Hold Down Detail

Status
Not open for further replies.

RFreund

Structural
Aug 14, 2010
1,875
US
I've attached two details - Is one, both or neither correct/typical?

I am also aware that Simpson makes hold downs which are more like straps that extend into the concrete but I'm 'neglecting' these for now.



EIT
 
Replies continue below

Recommended for you

The idea is typical for both and done all the time, but not with just straight rods unless they are threaded and set in epoxy.

If they are poured-in-place anchors, Simpson calls these SSTB abchors and they are usually used with HD type anchors. I believe the nomenclature has been changed in the recent Simpson catalog from A's to B's, and the values have changed too.

Mike McCann
MMC Engineering
 
I agree with msquared48. Though I usually add addition vertical blocks next to the rim broad under the post in section 1.

Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
 