I'm a structural engineer by training working on the client's side - We are designing a 40 story structure with 32m x 25m footprint. The building's lateral load system will be a center core with perimeter columns. Our structural engineering consultant is saying:
"the structural opening is needed to keep shear wall length less than 8m. These openings can be door opening but should be 1.2m away from the corner"
I've never heard of this shear wall length criteria and couldn't find any reference for it. I've always thought that the less opening the better - so I asked him what he needs it for. He attached a page from ASCE 7 highlighting the 25% of the Load carried by Moment Frame requirement. Then he mentioned that it's "engineering practice", required to resist seismic load:
The link beam will enter plastic
Then the "wall leg"
Then the frame will provide resistance
Is this common practice ?
I understand if it's because of ductility requirement imposed by ASCE 7-10 as per Table 12.2-1 Section D.
Also, he mentioned that if the wall leg is too long, the rotation capacity is too small, and that in engineering practice the maximum shear wall length is typically 8m. Which rotation capacity is this ?
"the structural opening is needed to keep shear wall length less than 8m. These openings can be door opening but should be 1.2m away from the corner"
I've never heard of this shear wall length criteria and couldn't find any reference for it. I've always thought that the less opening the better - so I asked him what he needs it for. He attached a page from ASCE 7 highlighting the 25% of the Load carried by Moment Frame requirement. Then he mentioned that it's "engineering practice", required to resist seismic load:
The link beam will enter plastic
Then the "wall leg"
Then the frame will provide resistance
Is this common practice ?
I understand if it's because of ductility requirement imposed by ASCE 7-10 as per Table 12.2-1 Section D.
Also, he mentioned that if the wall leg is too long, the rotation capacity is too small, and that in engineering practice the maximum shear wall length is typically 8m. Which rotation capacity is this ?