Hi Folks
as what is an IBC storage area cover with an overhead roof (but not on the side walls) classified outdoor or indoor
I am considering a sprinkler system in accordance with NFPA 400 and NFPA 13

for fire sprinkler protection at appear no other choice than deluge sprinkler over entire area ( automatics sprinkler with glass bulb will not result in reliable detection activation due to open side of shed.)
Deluge system will have drastic impact on the water demand



 
Replies continue below

Recommended for you

How many sq ft

What nasty stuff will be under it???

Is it attached to another building,,, or how many feet away will it be?

In the USA?
 
Hi CDAFD
storage : HYDROGEN PEROXIDE 50% concentration in 1,000 litre intermediate bulk containers, total volume ±60,000 litre
separate from other buildings 15 m away

 
I did not check the rest of the book

But unless there is something else in IFC or local requirement check your IFC edition for this

5004.13 Weather Protection
Where overhead noncombustible construction is provided for sheltering outdoor hazardous material storage areas, such storage shall not be considered indoor storage where the area is constructed in accordance with the requirements for weather protection as required by the International Building Code.
Exception: Storage of explosive materials shall be considered as indoor storage.
 