We have a current transducer that has a 4-20mA output. We are using twisted shielded cable. The length of wire is around 75 feet at most to the display device. When the shield is left ungrounded, we get the proper reading on the meter. When the shield is grounded, we get a triangle looking wave (AC from 90-120Hz up to 55V, so I am told) imposed on the 4-20mA signal. Only one end of the shield is grounded when this happens. The cause is not from where the cable is routed because we have temporarily ran wire on the floor with the same result. We have metered the cable to the pairs and there is no short to the pair. I do not have a cable part number yet but it seems there is something radiating in the vicinity of the cable. There are four exact systems and only two are doing what I described (these two are located by each other and the other two installations are about 50 feet away).
My thoughts on the potential cause is:
1. something is radiating in the vicinity of the cable, but grounding one end should take care of it
2. the impedance of the shield to the pairs is such that the radiated frequency causes a low impedance to the pair from the shield causing the problem (this seems unlikely to me)
3. sounds like it could be a second order harmonic issue but not familiar with sources of second order harmonics
4. Ground is likely a noisy ground but I am not familar with the plant layout
This is a power generation facility and the area this is in is the governor/exciter systems. Any advice or comments? I was trying to decide if a filter on the input to the meter would help anything like a ferrite core but think the frequency is to low for something like this.
Sorry for the vague info but I will post more info as it becomes available.
My thoughts on the potential cause is:
1. something is radiating in the vicinity of the cable, but grounding one end should take care of it
2. the impedance of the shield to the pairs is such that the radiated frequency causes a low impedance to the pair from the shield causing the problem (this seems unlikely to me)
3. sounds like it could be a second order harmonic issue but not familiar with sources of second order harmonics
4. Ground is likely a noisy ground but I am not familar with the plant layout
This is a power generation facility and the area this is in is the governor/exciter systems. Any advice or comments? I was trying to decide if a filter on the input to the meter would help anything like a ferrite core but think the frequency is to low for something like this.
Sorry for the vague info but I will post more info as it becomes available.