Not really.
Concept is that the shield currents that pass through the zero sequence CT have to be negated by returning the ground wire through the CT.
In case of 1-core cables, it is a challenge to center the cables in the CT window. This is to be paid careful attention.

Rompicherla Raghunath
 
The picture looks correct. What alternative is being proposed?
 