jimmy2times
Electrical
- Jun 26, 2007
- 138
I’m hoping to get some assistance with understanding some issues we are experience with our shore to ship power system and whether they could be having impact on corrosion of a ship. Basically our wharf structure sees noise potential when our shore power system is energised and this noise disappears when ship reverts to ship on board power generators. I know there are few guys on here who seem to have good knowledge on shore power systems and keen to hear their thoughts especially.
See attached sketch for basic overview of system.
We have two independent shore transformer substations, one feeding aft end of the ship and other feeding the fwd section.
System works on floating, isolated, neutral principal.
Given a healthy system I am trying to understand if there will be current flow through the ship to shore bond cable (see green cables on sketch).
From thinking it through, for the condition of healthy balance power system with no faults, could we expect some zero sequence current through the system capacitance to the ship’s metallic hull, via bonding cables, through wharf pier structure and then back to the source via transformer capacitance to wharf? Therefore would we expect even in a healthy system (with no faults) some low level current in the ship bonding cables.
Under a fault condition (e.g. bolted phase fault) on the ship side, would one expect this current in the bond cable to reduce if not, disappear? i.e The fault current flows through the faulted phase and then returning via the healthy capacitance of the other non-faulted phases on the ship, therefore bypassing the bond cable?
How do I go about estimating the network system capacitance, it is quite a large distributed system on board. Does anyone have any similar examples or references papers where the distributed network capacitance of a large network is reduced by a few rules of thumb, or is it considered I need to model this in detail in modelling package.
See attached sketch for basic overview of system.
We have two independent shore transformer substations, one feeding aft end of the ship and other feeding the fwd section.
System works on floating, isolated, neutral principal.
Given a healthy system I am trying to understand if there will be current flow through the ship to shore bond cable (see green cables on sketch).
From thinking it through, for the condition of healthy balance power system with no faults, could we expect some zero sequence current through the system capacitance to the ship’s metallic hull, via bonding cables, through wharf pier structure and then back to the source via transformer capacitance to wharf? Therefore would we expect even in a healthy system (with no faults) some low level current in the ship bonding cables.
Under a fault condition (e.g. bolted phase fault) on the ship side, would one expect this current in the bond cable to reduce if not, disappear? i.e The fault current flows through the faulted phase and then returning via the healthy capacitance of the other non-faulted phases on the ship, therefore bypassing the bond cable?
How do I go about estimating the network system capacitance, it is quite a large distributed system on board. Does anyone have any similar examples or references papers where the distributed network capacitance of a large network is reduced by a few rules of thumb, or is it considered I need to model this in detail in modelling package.