short cicuit data from client

Status
Not open for further replies.

SELEC

Electrical
Nov 12, 2005
64
I am doing a short circuit study for a system. The fault level on 28KV side is, R1= 6.78727 OHM, X1=19.19640 Ohm.

On the SLD, it also shows that, R1(pu)=0.6787pu, X1(pu)=1.7196pu. 100MVA base

The above data doesn't make sense to me. The short circuit current derived from the above data.
 
Replies continue below

Recommended for you

I just confirmed the data. The per unit data is right and the system source is very weak. From down sream, we have 40% loads are VFD controle, so I am really concerned about the harmonic distotion effect.

I am wondering if there is rule of thumb to calculate harmonic portion. or I have to run ETAP software.
 
My lead told me that if we took out filters from VFD, VFD would be more expensive. That doesn't make sense to me.
 
I'm certain that a filter in a VFD will cost more than one without.

Mike
 
The lead was probably refering to a 18 pulse VFD vs a 6 pulse. The 18 pulse VFD would help with curbing harmonics. He was probably saying it was cheaper to put filters on a 6 pulse VFD rather than buying a 18 pulse VFD.

Maybe?

Jason

Jason Buda, PE
Greenville, SC
jbuda54@yahoo.com
 