majesus
Electrical
- Aug 16, 2007
- 262
I am studing short circuit and arc flash analysis and I am using Etap to do some experiments. I noticed that when determining the short circuit current value whether it was 3 phase bolt, L-G, arc flash, etc, a motor's load factor did not contribute to the fault current. In other words, if the motor is loaded to 40% or 90% it does not make any difference for short cicuit analysis.
From my reasoning, the explaination for this is:
1) The purpose of the short circuit analysis is to calculate the maximum fault current, thus motors are assumed to have a 100% LF (ie, fully energized.)
2) In most cases only the motor's rotor contributes to interia/momentum. Generally speaking, a typical load does not have significant inertia that drives the motor into a generatative state. Typical non momentium loads are pumps and fans. (Regenerative systems such as conveyors going down hill, etc are an exception.)
Am I correct? I'm in learning mode, and always interested in reading your comments.
Thanks
From my reasoning, the explaination for this is:
1) The purpose of the short circuit analysis is to calculate the maximum fault current, thus motors are assumed to have a 100% LF (ie, fully energized.)
2) In most cases only the motor's rotor contributes to interia/momentum. Generally speaking, a typical load does not have significant inertia that drives the motor into a generatative state. Typical non momentium loads are pumps and fans. (Regenerative systems such as conveyors going down hill, etc are an exception.)
Am I correct? I'm in learning mode, and always interested in reading your comments.
Thanks