Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Short circuit asymmetrical factor 1

Status
Not open for further replies.

electrolitic

Electrical
Dec 9, 2007
105
Do I need to consider the calculated short circuit asymmetrical factor in case of arc fault in a MV system?
For bolted faults I already need to provide a zero crossing delay for safe breaker opening.
Thanks.
 
Replies continue below

Recommended for you

What is the purpose of the short circuit calculation? If it is for arc-flash, you can ignore any asymmetrical current if you are using IEEE 1584. If it is for equipment duty calculations, it will depend on the standard that the breaker was tested to.

Arcing fault have a lot of resistance (the arc), so the X/R ratio is generally low. This results in low dc offset current.

But no one can really answer your question without more information.
 
Thanks DPC. Considering the system high X/R ratio I need to provide an intentional time delay for the protection in order to
match the correct interrupting capacity of the breaker in case of bolted fault. The confirmation of lower X/R ratio (that implies low asymetrical factor) in case of arc fault by IEEE would permit a fast detection and a faster breaker actuation.
Am I correct?
 
In terms of dc offset current, you'd have to account for the worst case which is going to be a bolted fault. Arcing faults don't have any bearing on interrupting ratings (at least in my part of the world), since the current magnitude of an arcing fault is going to be less than a bolted fault.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor