I am doing a simple short circuit calc for a 4 plex. The fault current available is 15625 symmetrical amperes at the 120/240 volts.
I selected my bussman C value based on the 750 kcmil wire at 21,387
My calc looks as follows:
F = 2 x 75ft x 15625 / (21,387 x 240) = 0.45661
M = 1 / (1 + 0.45661) = 0.6652
SCA = 16,625 X 0.68652 = 10,727 A
So my question is about the AIC rating. Should I use a minimum rating of 10K AIC? I do not think there is a 11k AIC rating? Otherwise I would go with the 22k AIC.
Also when I change the distance lets say to 50 ft. It works inversely which goes against my logic. The distance is actually less than 75ft. With this inverse relationship shouldn't the distance be a minimum and not maximum? Right now I say that the conductor length is maximum 75ft.
Thank you for your help,