rbauerpe
Electrical
- Jul 25, 2003
- 1
A campus has a significant amount of underground distribution consisting of PILC cable in ductbank. Distribution feeders at 13.8 kv each serve groups of buildings with each building having a secondary unit substation with fused interrupter switch and medium voltage transformer. Distribution feeders that serve older sections of the campus (50 years or more) have current limiting reactors. The short circuit current from the utility is 25,000 amps. After going through the reactor the short circuit current is about 6,000 amps.
There are a number of S&C interrupter switches with SM-4 fuses that are rated at 12500 amps interrupting There are some interrupters that I could not get any information, brand or fusing. Manholes with PILC cable do not have separate grounds with the PILC cable, so the primary ground return is the lead cable sheath.
We will be replacing the main switchgear that was installed about 1965. When the switchgear is replaced we will inspect each reactor and determine if it should remain in service or it should be replaced. If the reactors are replaced I would like to install smaller reactors. Reduce short circuit to below 12500 amps.
I have not been able to determine what equipment is being served that required the short circuit current to be reduced to 6000 amps. I am thinking that the limitation might be the lead sheath on the cable. I have not tried to calculate the maximum allowed current on the sheath yet. The PILC cable is 4/0 awg and 350 kcmil.
Any suggestions as to what I should be looking for as the limiting factor that required the fault current to be reduced from 25000 amps to 6000 amps.
There are a number of S&C interrupter switches with SM-4 fuses that are rated at 12500 amps interrupting There are some interrupters that I could not get any information, brand or fusing. Manholes with PILC cable do not have separate grounds with the PILC cable, so the primary ground return is the lead cable sheath.
We will be replacing the main switchgear that was installed about 1965. When the switchgear is replaced we will inspect each reactor and determine if it should remain in service or it should be replaced. If the reactors are replaced I would like to install smaller reactors. Reduce short circuit to below 12500 amps.
I have not been able to determine what equipment is being served that required the short circuit current to be reduced to 6000 amps. I am thinking that the limitation might be the lead sheath on the cable. I have not tried to calculate the maximum allowed current on the sheath yet. The PILC cable is 4/0 awg and 350 kcmil.
Any suggestions as to what I should be looking for as the limiting factor that required the fault current to be reduced from 25000 amps to 6000 amps.