Wfg42438
Electrical
- Apr 10, 2017
- 70
Hello,
I wanted to confirm with others if there are any ANSI standards which recommend to consider the following items for L-G SC calculations:
[ul]
[li]Shunt admittances of non-rotating loads[/li]
[li][/li]
[li]Line Capacitances[/li]
[/ul]
So far i was able to see only IEC60909 2016 has the following description:
Shunt admittances of non-rotating loads shall be neglected in the positive-, the negative and
the zero-sequence system.
Line capacitances shall be neglected in the positive- and negative-sequence system. Line
capacitances in the zero-sequence system shall be taken into account in low-impedance
earthed networks having an earth-fault factor (see IEC 60027-1) higher than 1,4.
Please let me know if you know of any ANSI standards that provide some guidance on this item, thanks!