Short Circuit Contributors

Status
Not open for further replies.

nightfox1925

Electrical
Apr 3, 2006
567
I am interested to ask whether we should include Frequency converters, harmonic filters and capacitors as contributors and model them in calculating short circuit currents.

I was having an impression that motors connected to VFDs do not contribute that much and are negligible, same as capacitors and harmonic filters.

 
Replies continue below

Recommended for you

Regenerative drives can contribute to external faults, the others can be ignored. Capacitors actually can contribute some current, but are universally ignored for a variety of reasons.
 
Hi dpc, if it is not too much to ask, may I ask the variety of reasons why capacitors may be ignored (to educate myself further)?

 
Hi Nightfox. Mabey this will help. Consider the natural response decay of a discharging capacitor. Now plug some realistic values in for R and C. You will have an extremely fast decay which makes the initial condition insignificant. Hope this helps.

BOb
 
Normally the power factor of fault current is very low - the current is highly lagging. Whatever capacitor fault current that occurs will be about 180 degrees out of phase with the inductive current. Also, the capacitor fault decays very quickly - normally within a cycle.

There is a lengthy discussion of capacitor fault currents in Conrad St. Pierre's book "A Practical Guide to Short Circuit Calculations."

But I don't think ANSI or IEC standards for short circuit calcs have any guidance regarding capacitors.
 
Motors on non-regenerative drives can be ignored only if there is not a bypass contactor. Regenerative drives will contribute some but not as high a magnitude as a motor directly on the line.
 
Thank you very much for all your inputs. I will order the St. Pierrie Book.

Thanks Rags004 for the R-L-C circuit recap.

Thank you for the reminding me also about the bypass contactors...I am learning a lot from this forum.

 
Hi nightfox1925,

As a supplier of complete installations comprising converters and harmonic filters, I've been working on Isc calculation on marine HV networks. My conclusions are :

1. For converters:
Only converters with thyristor bridges on network side (ie static frequency converters) can contribute to a short-circuit. They will contribute only if the short-circuit occurs when the drive is regenerating. You can find quite good explanations in IEC61363-1. Calculations are quite difficult as the contribution depends on the operating point of the machine at the time the fault occurs;

2. For harmonic filters and capacitor banks:
Obviously they are never taken into account. Our calculations on a few typical projects have shown that due to the time constants of these R-L-C circuits, they do not contribute to the peak value of the short-circuit current, wich is usually the most critical value to verify.

Hope we are in phase guys?


 