NickParker
Electrical
- Sep 1, 2017
- 420
Say if a MCC is rated for a short circuit capacity of 25kA, What is the short circuit at the load end terminal? this is to check the short circuit withstand check of the cables to that particular load.
I have the cable impedance for the length till the said load,
The calculation is as follows,
SC current at the load terminal = VL-L / (1.732 x (System impedance + Cable impedance)
Where,
VL-L = Line to Line voltage
System impedance = VL-L/ (1.732 x 25kA)
Is my approach correct?
I have the cable impedance for the length till the said load,
The calculation is as follows,
SC current at the load terminal = VL-L / (1.732 x (System impedance + Cable impedance)
Where,
VL-L = Line to Line voltage
System impedance = VL-L/ (1.732 x 25kA)
Is my approach correct?