Hello everybody...
Let say we have two transformers (please don't bother with transformers data, they are only to get the pricipal on how to calculate):
1. 20/10kV, uk=8%, S=40MVA, YNd1
2. 10/6.6kV, uk=6%, S=20MVA, DYn11
If we would like to make stability test of 20/10kV transformer on way that we make 3ph SC on 6.6kV side, and inject 400V on 20kV side, how much current we will get on 3ph SC on 6.6kV side, and how much current we will have on injection point on 20kV side?
I get 115A on 6.6kV side, and 38,3A on injection point on 20kV side. Am I close to the correct values?
Things that I would like to know:
-how to calculate impedance of transformer in this case. Are they calulate on 20kV base as we have injection on this side.?
-does and, if does, how vector group of transformers influent on calculations?
Thank you all....