I received short circuit calculation on the switchboard however, the short circuit level needs to be lowered in order to select Circuit Breaker with less fault current in aspect of cost.
I therefore suggest to adjust constants values such as subtransient reactance on the four generators. If constants are increased I know that voltage drop should be taken consideration. Except voltage drop, is there any other adverse effects I should consider in adjusting constants ?
The constants are as below ;
Xd : 240%, T'd : 0.1478 sec
X'd : 25% T''d:0.0055 sec
X"d : 12.7% Ta : 0.04sec
RA : 0.8%