Hi gentlemen, I am presently making some evaluation of an existing protection scheme. I have here an 11kV switchgear with three bus bar sections (bus A, B and C) connected by normally closed tie breakers. There are three incomers (one incomer in each bus section).
Neglecting load contribtions and considering only the incomer contributions. If I have a three phase short circuit at an outgoing feeder at Bus A, upstream incoming contribution of equal value (say 3000A)will flow through the three incomers. Will CT of the bus tie connecting bus B-C sense 3000A and the CT of the bus tie connecting bus A-B see 2 x 3000A = 6000A considering current flow direction to the faulted outgoing feeder at bus A? Or will both bus ties see total current of 3 x 3000A=9000A regardless of any outgoing feeder fault?
Thanks and best regards...
GO PLACIDLY, AMIDST THE NOISE AND HASTE-Desiderata
Neglecting load contribtions and considering only the incomer contributions. If I have a three phase short circuit at an outgoing feeder at Bus A, upstream incoming contribution of equal value (say 3000A)will flow through the three incomers. Will CT of the bus tie connecting bus B-C sense 3000A and the CT of the bus tie connecting bus A-B see 2 x 3000A = 6000A considering current flow direction to the faulted outgoing feeder at bus A? Or will both bus ties see total current of 3 x 3000A=9000A regardless of any outgoing feeder fault?