For those of you that do short circuit studies, I have the following. What has been your experience with the accepted convention for assuming motor contribution when specific motor data is unavailable?
Is it common to assume a value (say 25% of the main switchgear size) and put a lumped motor model at the main switchgear. This is more simplistic than a motor model at each panel, but for small systems may lead to similar results.
I always try to model large motors based on actual data, but for a planning study, that data is not present.
Thanks
Is it common to assume a value (say 25% of the main switchgear size) and put a lumped motor model at the main switchgear. This is more simplistic than a motor model at each panel, but for small systems may lead to similar results.
I always try to model large motors based on actual data, but for a planning study, that data is not present.