AusLee
Electrical
- Sep 22, 2004
- 259
Hello,
I have 2x1,000kVA transformers in a building fed from the same 15kV ring. Each TR feeds a separate MDB so the secondary sides are not in parallel but a tie breaker is provided so they May be put in parrallel sometime for a given reason.
The local authority wants to read only 1 watt meter so i have the following MV cells arrangement:
Ring In-Ring Out-Metering-Out TR1-Out TR2
The breakers (no fuses) in "Out TR1" and "Out TR2" are 25kA because the transformers are 1000kVA 15kV/400V and network Pcc=500MVA. My question is: what would be the short circuit rating of the breaker in the Metering cell? 25 or 50kA and why?
In case it should be 50kA, can you please point out a product on the market? i know Merlin Gerin SM6 but they go up to 25kA only for equipment under 24kV.
Thanks.
I have 2x1,000kVA transformers in a building fed from the same 15kV ring. Each TR feeds a separate MDB so the secondary sides are not in parallel but a tie breaker is provided so they May be put in parrallel sometime for a given reason.
The local authority wants to read only 1 watt meter so i have the following MV cells arrangement:
Ring In-Ring Out-Metering-Out TR1-Out TR2
The breakers (no fuses) in "Out TR1" and "Out TR2" are 25kA because the transformers are 1000kVA 15kV/400V and network Pcc=500MVA. My question is: what would be the short circuit rating of the breaker in the Metering cell? 25 or 50kA and why?
In case it should be 50kA, can you please point out a product on the market? i know Merlin Gerin SM6 but they go up to 25kA only for equipment under 24kV.
Thanks.