The software that I'm using to perform a short circuit study asks me the following information when I insert a 2 winding transformer:
KVA/phase, Z+(pu), Zo(pu), configuration, grounding impedance (ohms).
The transformers that I'm considering are 3 phase banks (single phase transformers connected to the desired 3 phase config.).
For example I have three 500 kVA single phase transformers, each with an impedance of 6.04 % (0.85+j5.97) and they are connected delta-wye (600 V - 25 kV).
When I enter this data into the program that I'm using, is it correct to say that,
1.) KVA/phase is 500 kVA (obvious)
2.) Z+ = 0.0085 + j0.0597
I was under the impression that for delta-wye transformers, Zo is the zero-sequence impedance to ground, seen at the wye-side of the transformer.
Is it correct to assume that Z+ and Zo should be identical for transformers made up of single-phase banks ?
If I don't know the impedance of the ground.....will this pose a problem ? Is it usually a critical value ?
Thanks in advance
KVA/phase, Z+(pu), Zo(pu), configuration, grounding impedance (ohms).
The transformers that I'm considering are 3 phase banks (single phase transformers connected to the desired 3 phase config.).
For example I have three 500 kVA single phase transformers, each with an impedance of 6.04 % (0.85+j5.97) and they are connected delta-wye (600 V - 25 kV).
When I enter this data into the program that I'm using, is it correct to say that,
1.) KVA/phase is 500 kVA (obvious)
2.) Z+ = 0.0085 + j0.0597
I was under the impression that for delta-wye transformers, Zo is the zero-sequence impedance to ground, seen at the wye-side of the transformer.
Is it correct to assume that Z+ and Zo should be identical for transformers made up of single-phase banks ?
If I don't know the impedance of the ground.....will this pose a problem ? Is it usually a critical value ?
Thanks in advance