polarseltzer
Industrial
- Mar 27, 2013
- 6
I understand that switchboards are built to have a withstand time rating of 3 cycles. Now that is at the rating of the switchboard, for example 100kA. I am struggling with a coordination issue where I can turn off the instantaneous setting of the main breaker (SQD Masterpact NW40H3, Micrologic 6.0A 4000A plug) which would improve the coordination with feeder breakers. My concern is that this defeats the instantaneous protection for the switchboard. The breaker does have an instantaneous override of 85kA. The maximum fault current available is slightly less than 25kA. So is there a damage type curve for switchboards that would show for example that the switchboard can withstand 25kA for 2 seconds? It would be similar to a conductor damage curve. With the instantaneous turned off the breaker would trip around 0.3 secs(18 cycles, does this provide adequate protection for the switchboard?