leathermanp

Mechanical
Sep 17, 2009
7
I designed a hospital roof helipad drain system around fuel gas code considering life safety issues of patients. I specified ASTM A53 schedule 40 steel pipe with welded joints (Schedule 40 ERW with welded joints was installed). Will the corrosion characteristic of this pipe support the storm water requirements? What would be the life expectancy of this pipe in a storm water application?


 
Replies continue below

Recommended for you

That's just the most garden variety of carbon steels. Schedule 40 thickness relative to the diameter is not thin. I don't know exactly how long it would last, but my sense is that the life would be several decades.

I work in the water treatment industry, and we have potable water lines in our pump plants that are still in service after 70 years. Stormwater, if it's super soft, may be a bit more corrosive. But the time to failure should be substantial.

You didn't state, but I'm assuming the pipe is black pipe. The A53 standard covers hot dipped galvanized as well.
 
As long as there line will actually drain you should be fine. If there are sections with little or no slope where water might stand then you may have issues.

= = = = = = = = = = = = = = = = = = = =