  • Congratulations Danlap on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!
Should secondary protection consider xfmr inrush current?
Dvhez
55
Hi everyone,
I’m setting up protection for a 13.8 kV to 400 V transformer and wondering how much inrush current should influence secondary-side protection. I know primary protection (relays, fuses) is typically set to tolerate inrush, but what about MCCBs or relays on the 400 V side?
At the secondary I have a Micrologic 2.3 which doesn't allow me to add time delay in order to avoid the transformer inrush current. The only way is to increase the Short-Time pickup, but doing this I "cross" all the other devices that are in the primary side.
Thanks!
Then the only inrush you need to cover will be from the down line transformers.
Thank you Stevenal. I'm sorry for asking, but did you mean that I need to set the primary side devices above the inrush curve meanwhile the devices on the secondary side (load) are not required to be above this inrush current in a TCC graph?
If so, do you know which standard (US) talk about this?
Yes. I know of no standard, just physics. Inrush comes from the source side.
Think about it;
The primary inrush is fed from the grid.
Where would an inrush on the secondary go?
The maximum % inrush of common loads is typically less than the maximum % inrush of the transformer primary.
Thee only time I had an issue was when the undersized fuse on the primary of a 120/24 Volt control transformer would allow the unloaded transformer to energize but would open when the transformer was energized with a load connected.
With the proper protection on the primary, we don't see a problem with secondary loads.
