Almost all is said above. Seen from an European (and practical) side 6 bar (very near 87 psi) is a normal air supply pressure often used for air supply for valve-actuators and instrumentation. A lot of actuators is designed operated at this pressure, and will require, say, 4-6 bars for a normal valve operation.
On the other hand a normal EU class for valves is 10 bar (150 psig), and the whole valve, including actuator and membrane is very often designed for this, but not always.
The choice for a limitation of the membrane (allowed) operational pressure may ether be practical, based on engineering/design reasons, or based on price. What does the vendor say? Size, experience and availability of material might also be factors here.
Again: you will not necessarily get a poorer product with a lower expected life-time by choosing a membrane with higher allowable working pressure, you might need a less elastic material with different qualities.