i'm desinging fire sprinkler systems for houses per nfpa 13d. we are running into problemes w/ acsessing vaulted ceilinig areas w/ pendent heads because of beams that are not drillable. my installer decided to use horizontal sidewalls instead of pendants. well when he gave me a redline drwg of how it was installed so i could submit an as-built; i noticed that he was using sidewall heads perpendicular to the slope which is not allowed. further research says i can't use a sidewall unless i run it parrallel to the slope and at the highest point of the peak (nfpa 13 2007 edition8.7.4.2.2). but the max slope is 2:12 and i'm dealing w/ anything from 8:12 to 12:12. and even if i had a 2:12 theres 18" deep exposed beams that run along the peak. so i guess my question is: is there a head out there or an idea any of you may have that solves this problem? thank you all in advance.
tony
tony