skdesigner
Mechanical
- Aug 17, 2010
- 432
Mundane question for a thursday afternoon.
NFPA 13 2010 8.7.3.1.7 Permits sidewalls under overhead doors in an otherwise ordinary hazard area to be spaced for light hazard.
8.3.3.1 would dictate these sprinklers have quick response elements.
8.3.3.2 then requires that if the sidewalls are quick response, all sprinklers in the compartment shall be quick response.
So, if we're talking an OH2 pre-eng building with 30' AFF deck (i.e can't use QR to reduce the remote area), are the uprights now required to be QR because of 8.3.3.2?
I've always assumed that "protection area and maximum spacing for light hazard" is different than actually being a light hazard occupancy, but I like to second guess myself.
What says the forum?
NFPA 13 2010 8.7.3.1.7 Permits sidewalls under overhead doors in an otherwise ordinary hazard area to be spaced for light hazard.
8.3.3.1 would dictate these sprinklers have quick response elements.
8.3.3.2 then requires that if the sidewalls are quick response, all sprinklers in the compartment shall be quick response.
So, if we're talking an OH2 pre-eng building with 30' AFF deck (i.e can't use QR to reduce the remote area), are the uprights now required to be QR because of 8.3.3.2?
I've always assumed that "protection area and maximum spacing for light hazard" is different than actually being a light hazard occupancy, but I like to second guess myself.
What says the forum?