I've asked this question before, but I can't find it anywhere in the forums. I'll try again.
Has anyone experienced any problems with the Siemens G120 VFD's?
We have experienced flash overs between the dc link bus bars which destroys the main rectifier. When the faulty inverters are changed, we remove the bus bars to reduce the possibility of a similar failure.
When we talk to Siemens engineers about the problem, they infer that it is an ingress of carbon particles (the inverters are used for a newly installed carbon fibre production line) which reduces the resistivity of the air separating the bus bars to the point of flash-over. The panels which contain the VFD's are remote from the production line and great efforts are used to ensure that there is no ingress of contaminants.
Has anyone experienced any problems with the Siemens G120 VFD's?
We have experienced flash overs between the dc link bus bars which destroys the main rectifier. When the faulty inverters are changed, we remove the bus bars to reduce the possibility of a similar failure.
When we talk to Siemens engineers about the problem, they infer that it is an ingress of carbon particles (the inverters are used for a newly installed carbon fibre production line) which reduces the resistivity of the air separating the bus bars to the point of flash-over. The panels which contain the VFD's are remote from the production line and great efforts are used to ensure that there is no ingress of contaminants.