Our facility has a power management system based on a Siemens S7 PLC polling about 100 Siemens 9610 multifunction relays which are daisy-chained together with 4-wire RS485 serial cable. We recently experienced a total loss of facility power, and the power monitoring system completely froze up for at least two minutes right when we needed it most. We have gotten very little support from the vendor in resolving this issue, so I am hoping that some of you talented individuals on this forum can help point me in the right direction. My present assumption is that the most likely answer is that simultaneous alarming of over 100 remote terminal units attempting to alert the central PLC over daisy-chained serial cable caused a communications bottleneck which lead to a system hangup. Does this seem reasonable, or am I chasing a red herring? Any thoughts would be greatly appreciated.