I am application sales engineer for a Fan Manufacturer. We sold a Fiberglass Fan for a Sewer Lift Station. Basic exhaust system to remove H2S in Deep Well. Fan is a 20" Dia Tubeaxial (No Vanes on Fan).
Problem: Contractor purchased and installed a 2 Silencer, one Inlet and one Discharge located directly, within 3 In. of Fan Inlet and Discharge Flange. Fan war reported deficient on Flow after being tested by a Certified Air Balance Co. We did not furnish silencers or provide any info to the silencer manufacturer.
Each Silencer is has a set of internal turning vanes. See Picture.
I don't know anything of these silencers, first time I have ever encountered turning vanes in a silencer. I doubt the Silencer Manufacturer designed the Stationary Silencer Vane Pitch, Camber, Length, Quantity of Turning Vanes, with respect or consideration of "Tuning the Silencer Vanes” specific to this 20" FRP Fan.
Anyone encounter a similar situation? Anyone care to comment as to what sort of system effect would or could occur if these Silencer Vanes were not designed specific for this Fan?
Problem: Contractor purchased and installed a 2 Silencer, one Inlet and one Discharge located directly, within 3 In. of Fan Inlet and Discharge Flange. Fan war reported deficient on Flow after being tested by a Certified Air Balance Co. We did not furnish silencers or provide any info to the silencer manufacturer.
Each Silencer is has a set of internal turning vanes. See Picture.
I don't know anything of these silencers, first time I have ever encountered turning vanes in a silencer. I doubt the Silencer Manufacturer designed the Stationary Silencer Vane Pitch, Camber, Length, Quantity of Turning Vanes, with respect or consideration of "Tuning the Silencer Vanes” specific to this 20" FRP Fan.
Anyone encounter a similar situation? Anyone care to comment as to what sort of system effect would or could occur if these Silencer Vanes were not designed specific for this Fan?