If you use Isc=Ifla/z, and you're designing the system (ie you're not looking at a nameplate), you should adjust z downward by 7.5%. In other words, min. imp for a 5.75% transformer would actually be 5.3%, unless the transformer was small (I'm not sure of the rating, but it's quite small, like 75 kva), in which case you use 10%.