drhenne
Civil/Environmental
- Aug 2, 2000
- 15
We want to create 3 lots for the construction of single family residences. A town sewer and manhole is adjacent to the one of the lots. The other two lots will require a sewer extension about 400 feet long. Local and State ordinances require 2 fps velocity for an 8 inch pvc pipe flowing full. Minimum grade is .005 ft/ft. Existing grade and sewer inlet conditions would allow the extension grade to be as steep as .01 ft/ft. My pipe-full calculations using mannings (N=.013)indicate a velocity of 2.45 f/s, which would be satisfactory per ordinance. My concern is this - will 3 units provide enough flow for the sewer to operate properly, considering scouring, etc ? The required daily design flow per unit is 270 gpd. This is probably a routine problem for an engineer, but I am stuck. Could someone please show me the proper way to approach this design question?