Inder76
Electrical
- Aug 2, 2007
- 9
Hi,...
This is my second. question on this forum. I am happy with my first question response.
Thanks to all who contributed.
# 1 : I am using ETAP for a short circuit calcs. I am pluging the info from utility.
As per the help file,
3 Phase Short Circuit MVA= sqrt(3) * V(L-L)* Ifault(3 Phase)
This makes sense to me;
Now
Single phase short circuit MVA= sqrt(3)*V(L-L)*ifault(1-Phase ground fault)
It did not make sense to me. I spoke to the tech support but looks like these people are more trained for software using issues and cannot answer any theortical issues like this.
Could you advise?
#2 After three phase analysis, I will be looking in to ground fault for grounding design;
Fotunately or unfotunately, the ground fault current is zero:
The transformer can be fed from two feeders:
So I have to consider the worst case contribution of ground fault for grid design. Either one of the feeders will feed at one time.
Feeder #1 is fed from Delta/Delta. That means no ground fault on my transformer (Delta/Star grounded) primary.
Feeder#2 is fed from Star(open)/Star(solidly grounded).
Again no ground fault current, I guess zero sequence for an ungrounded star does not lead to ground fault.
Now what value do I use for my ground fault ?
Here is the catch, when I do a double line to ground fault(on my primary), it gives me ground fault. Why is that ?
Thanks in anticipation for your effort.
This is my second. question on this forum. I am happy with my first question response.
Thanks to all who contributed.
# 1 : I am using ETAP for a short circuit calcs. I am pluging the info from utility.
As per the help file,
3 Phase Short Circuit MVA= sqrt(3) * V(L-L)* Ifault(3 Phase)
This makes sense to me;
Now
Single phase short circuit MVA= sqrt(3)*V(L-L)*ifault(1-Phase ground fault)
It did not make sense to me. I spoke to the tech support but looks like these people are more trained for software using issues and cannot answer any theortical issues like this.
Could you advise?
#2 After three phase analysis, I will be looking in to ground fault for grounding design;
Fotunately or unfotunately, the ground fault current is zero:
The transformer can be fed from two feeders:
So I have to consider the worst case contribution of ground fault for grid design. Either one of the feeders will feed at one time.
Feeder #1 is fed from Delta/Delta. That means no ground fault on my transformer (Delta/Star grounded) primary.
Feeder#2 is fed from Star(open)/Star(solidly grounded).
Again no ground fault current, I guess zero sequence for an ungrounded star does not lead to ground fault.
Now what value do I use for my ground fault ?
Here is the catch, when I do a double line to ground fault(on my primary), it gives me ground fault. Why is that ?
Thanks in anticipation for your effort.