Now, once you do specify a double hole (or four hole) bolted connector, YOU have to be able to get enough room AFTER the connector plate for the extra length of wires and cable bends to be routed and pulled and hooked up - which are NOT small for 1 and 2 inch dia copper cables) before interferences: hole in the concrete for example, nearby equipment housings, the other end of the wire or the other end of the equipment housing where the cable penetration is.
So, for the new turbine exciter, we have 4x 2 inch diameter leads that had to come vertically up through a 6 foot thick concrete floor. Then bend in a complex loop to be bolted horizontally to the copper plates on the exciter. The resulting "cable loops" in midair blocked access through the exciter equipment housing on that one side, so they needed an extra door in the housing. It was tight enough that to get room for the lowest of the cable loop, we "rounded off" the drilled holes in the concrete to be able to start the bends a little bit under the floor level.