xtal01
Mechanical
- Mar 15, 2012
- 143
OK, dumb question ...
I have a stairway to the second floor of my shop.
The floor is 16" TJI's (wood I)
The stairway is against the wall with the floor joists running parallel.
To frame the stairway, I am going to use an LVL rather than just another TJI. If for no other reason, it will be something solid to attache the railing on the upper floor to.
I did run on the Weyerhauser Forte software ... easily passes (obviously if a TJI passes than a LVL of the same depth will pass).
I only need a single LVL .. worst case only loaded to 40% of its' max
I was looking at a few houses in the area .. they all used a double LVL at the stairway opening .... they may have just needed because of the length and load or maybe there will be a wall above it or ?
As this is the edge of the floor do I need two? Is there anything I am missing?
Just wanted to make sure I am doing everything right.
Thanks ... Mike
I have a stairway to the second floor of my shop.
The floor is 16" TJI's (wood I)
The stairway is against the wall with the floor joists running parallel.
To frame the stairway, I am going to use an LVL rather than just another TJI. If for no other reason, it will be something solid to attache the railing on the upper floor to.
I did run on the Weyerhauser Forte software ... easily passes (obviously if a TJI passes than a LVL of the same depth will pass).
I only need a single LVL .. worst case only loaded to 40% of its' max
I was looking at a few houses in the area .. they all used a double LVL at the stairway opening .... they may have just needed because of the length and load or maybe there will be a wall above it or ?
As this is the edge of the floor do I need two? Is there anything I am missing?
Just wanted to make sure I am doing everything right.
Thanks ... Mike