There is a discussion, going on in a different forum (so far it has gone on for a total of 15 pages) concerning the loading of a wye connected transformer.
The only important fact is the transformer in question would have a 208Y/120 connected secondary. With a single 208V 10A resistive load connected to terminals X1 and X2 of the transformer (X3 is not connected).
What the arguement seems to be about is that "the apparent power in the load" is different than "the apparent power delivered by the transformers".
Quote (Rattus)...
In a 120/208V wye, with a single 208V, 10A load, what is the apparent power delivered by the two transformers supplying that load?
Most would say 2.08KVA.
However, if one considers the transformers individually, one sees that each transformer delivers 120Vx10A = 1.2KVA for a total loading of 2.4KVA.
...quote
Is this a trick with numbers or a valid method for analysing transformers?