Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

single phase motor -- current 1

Status
Not open for further replies.

rwelk

Materials
Joined
Jul 21, 2004
Messages
26
Location
CA
If I have a 120V - single phase motor, is current simply equal to power/voltage?
 

I= (HP*746)/(V*PF*EFF)

HP= motor power output ( in the shaft)
V = Voltage
PF = Power Factor (per unit)
EFF = Motor Efficiency
 
Not exactly, you still have to take the power factor into consideration. The actual formula for current in a 1 phase motor is: I = WATTS / (V x PF)
 
what is the power factor? Can I determine that, or is that a characteristic of the motor? If i can't determine it, can I estimate reasonably?

This motor is ''small'', 0.5hp, 1725rpm, 120V/1ph/60hz used to run a small fan. Unfortunately, those are the only specs I have on the motor.

cheers
 
one more thing, I don't know if it ac or dc, should that matter? The specs i have are from the company I bought the fan from, and not the motor, and that is partly why I have such limited information.
 
This is an AC motor as the frequency 60 HZ is in the nameplate data. The formula is for AC moors.

The Power Factor and Efficiency are defined by the motor construction. If you do not have information from the manufacturer you must assume them.For this small motor the product EFF*PF could be around 0.64, then the spected full load (0.5 HP) current is:

Ifl = 0.5HP*746/(120*.64) = 4.85 Amperes.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top