Power0020
Electrical
- Jun 11, 2014
- 303
Math wise the ground fault current is If= 3E/(Z1+Z2+Z0)
where E is the phase voltage, Z1 is positive seq. impedance, Z2 is negative sequence impedance and Z0 is zero sequence impedance. with transmission lines and cables it is common to assume that Z1=Z2=Z then If = 3E/(2Z+Z0).
The zero sequence impedance included 3 times any ground connected resistance (e.g. NER, tower footing resistance,...etc)
However, I have seen some literature calculate the fault current with a simple KVL loop including phase voltage as a source, earth loop resistance/impedance including grid resistance and tower footing, no consideration for any sequence impedance.
If=E/ZE
I am confused!
any clues?