Hello All hope someone can help me.
I am working on a project which requires single phase to three phase conversion for some motors. This is being accomplished by using VFDs, ABB ACH550-UH HVAC Drives. There are a total of 4 drives being used to power 4 seperate motors. 3 of the drive motor combinations work well, but 1 drive motor combination displays a fault, and does not operate correctly.
The specifics are below:
The motor is 5 HP motor 240 Volt, the drive has been derated because of the phase conversion and is a 10HP drive.
When the drive first powers the motor, the motor acts like it is single phasing and starts with a jerking action, and continues to vibrate like crazy. The motor has been removed and tested by a motorshop with 3 phase power,and came back with no errors.
One of the legs of the power from the drive to the motor was drawing a lot more current. 2 legs were drawing around 11.8 amps, and the other leg was drawing 15.86 amps (at 45hz before drive faults). All electrical connections were double checked and found to be tight.
The drive will only run up to around 45hz (with much shacking and vibration of the motor) before it faults. The error code is Supply Phase - Ripple voltage in the DC link is too high.
My thoughts are that for some reason the capacitor in the drive is either not big enough, or is not functioning properly, which is causing to big a ripple voltage.
I am recommending a replacement of the drive, and possibly a larger drive, but because this project is so far North and the expense to get the drive flown in is fairly high, I want to make sure that I haven't overlooked anything.
Any ideas or recommendations?
Thanks in advance,
Jamie
I am working on a project which requires single phase to three phase conversion for some motors. This is being accomplished by using VFDs, ABB ACH550-UH HVAC Drives. There are a total of 4 drives being used to power 4 seperate motors. 3 of the drive motor combinations work well, but 1 drive motor combination displays a fault, and does not operate correctly.
The specifics are below:
The motor is 5 HP motor 240 Volt, the drive has been derated because of the phase conversion and is a 10HP drive.
When the drive first powers the motor, the motor acts like it is single phasing and starts with a jerking action, and continues to vibrate like crazy. The motor has been removed and tested by a motorshop with 3 phase power,and came back with no errors.
One of the legs of the power from the drive to the motor was drawing a lot more current. 2 legs were drawing around 11.8 amps, and the other leg was drawing 15.86 amps (at 45hz before drive faults). All electrical connections were double checked and found to be tight.
The drive will only run up to around 45hz (with much shacking and vibration of the motor) before it faults. The error code is Supply Phase - Ripple voltage in the DC link is too high.
My thoughts are that for some reason the capacitor in the drive is either not big enough, or is not functioning properly, which is causing to big a ripple voltage.
I am recommending a replacement of the drive, and possibly a larger drive, but because this project is so far North and the expense to get the drive flown in is fairly high, I want to make sure that I haven't overlooked anything.
Any ideas or recommendations?