tem1234
Electrical
- Jun 13, 2007
- 192
Hi everyone, It's my first post here.
I have to do an arc flash study where the utility have a lot of 1 phase transformer 25kV to 120/240V. The client want us to calculate the short circuit current and the arc flash hazard at the secondary of theses transformers.
I red that the calculation must be done for an equivalent 3 phases system for the arc flash, but what's the equivalent? If I want the same short circuit current as the single phase, i must take a transformer with a bigger kVA, but is it realistic? Does the equivalent system is the one with the same short circuit current or the same power?
And for a 3 phase system, you can stop the arc flash if the transformer is 125kVA or less (at 240V), but if it's a single phase, do you stop at 125 kVA or 125/3 = 42 kVA?
Thank you
I have to do an arc flash study where the utility have a lot of 1 phase transformer 25kV to 120/240V. The client want us to calculate the short circuit current and the arc flash hazard at the secondary of theses transformers.
I red that the calculation must be done for an equivalent 3 phases system for the arc flash, but what's the equivalent? If I want the same short circuit current as the single phase, i must take a transformer with a bigger kVA, but is it realistic? Does the equivalent system is the one with the same short circuit current or the same power?