I have been trying to convince my fellows here at work but rather posting this to get second opinion.
Say we have a single phase 13.2 kV - 240/120 V pole type transformer with secondary 240/120 V single phase 3 wire (X1-X2-X3). The H2 is connected to a grounded primary conductor (typical to this type of service)and the transformer tank is bonded to the primary grounded conductor.
HOWEVER, the X1-X2 terminals are connected to the UNGROUNDED service drop conductors and X3 terminal is floating.
My concern is that this violates NEC as there is no grounded conductor in the service drop where the customer can make the necessary ground return path via main bonding jumper at the service equipment. My fellow argued that since the transformer tank is bonded to the primary grounded conductor, it should be ok.
I informed him that the transformer primary and secondary windings are isolated grounding-wise and a ground fault at the secondary MUST FLOW BACK TO THE SECONDARY winding and if one of the secondary terminals (X2 if 240V is only required OR X3 if 120 V is required) is not solidly grounded, the equivalent zero-sequence is OPEN-CIRCUITED at the secondary side and hence will be forced to flow back through the soil ground resistance which is not an effective ground return path.
Is my explanation correct and accurate?
Regards,
Say we have a single phase 13.2 kV - 240/120 V pole type transformer with secondary 240/120 V single phase 3 wire (X1-X2-X3). The H2 is connected to a grounded primary conductor (typical to this type of service)and the transformer tank is bonded to the primary grounded conductor.
HOWEVER, the X1-X2 terminals are connected to the UNGROUNDED service drop conductors and X3 terminal is floating.
My concern is that this violates NEC as there is no grounded conductor in the service drop where the customer can make the necessary ground return path via main bonding jumper at the service equipment. My fellow argued that since the transformer tank is bonded to the primary grounded conductor, it should be ok.
I informed him that the transformer primary and secondary windings are isolated grounding-wise and a ground fault at the secondary MUST FLOW BACK TO THE SECONDARY winding and if one of the secondary terminals (X2 if 240V is only required OR X3 if 120 V is required) is not solidly grounded, the equivalent zero-sequence is OPEN-CIRCUITED at the secondary side and hence will be forced to flow back through the soil ground resistance which is not an effective ground return path.
Is my explanation correct and accurate?
Regards,