podobing
Electrical
- Jan 28, 2013
- 49
To all,
We have a customer that has a 12,470 volt, three phase, resistance grounded power system. The secondary of the source transformer is wye connected. The neutral grounding resistor resistor limits the line to ground fault current to 15 amperes. They want to install two single phase voltage regulators to maintain the system voltage during hard motor starts. The regulators would be connected in an "open delta" type of arrangement. The two regulators are connected:
Regulator 1: Terminal S to X1 of source transformer; SL to X2 of source transformer; L to load phase A
Regulator 2; Terminal S to X3 of source transformer; SL to X2 of source transformer; L to load phase C
X2 of the source transformer also becomes load phase B.
There is also a VCB between the source transformer and the proposed site of the regulators, but tI thought that may just confuse my explanation of the regulator connections.
I explained that I did not think this plan would work properly as the regulators would resemble a delta - delta transformer and would not be able to handle zero sequence currents in the event of a ground fault. Other than putting a short on the load circuit, I do not know how to prove or disprove what I just wrote. Can anyone help me with this problem?
Regards,
Dave
We have a customer that has a 12,470 volt, three phase, resistance grounded power system. The secondary of the source transformer is wye connected. The neutral grounding resistor resistor limits the line to ground fault current to 15 amperes. They want to install two single phase voltage regulators to maintain the system voltage during hard motor starts. The regulators would be connected in an "open delta" type of arrangement. The two regulators are connected:
Regulator 1: Terminal S to X1 of source transformer; SL to X2 of source transformer; L to load phase A
Regulator 2; Terminal S to X3 of source transformer; SL to X2 of source transformer; L to load phase C
X2 of the source transformer also becomes load phase B.
There is also a VCB between the source transformer and the proposed site of the regulators, but tI thought that may just confuse my explanation of the regulator connections.
I explained that I did not think this plan would work properly as the regulators would resemble a delta - delta transformer and would not be able to handle zero sequence currents in the event of a ground fault. Other than putting a short on the load circuit, I do not know how to prove or disprove what I just wrote. Can anyone help me with this problem?
Regards,
Dave