kntx
Mechanical
- Feb 16, 2006
- 5
I'm attempting to understand a problem we had several weeks ago. I'm a mechanical engineer, so I probably don't have some of the terminology straight either.
We had several failures in the circuit breakers on equipment fed from our 5B 480V bus during a startup on our power plant. In one of the breakers a control transformer was burned up, some relays powered from the 5B bus were melted. We found in the circuit breaker from the 5B station service transformer to the 5B 480 Volt bus, the "b" phase "stab" was bent down and was apparently not making good contact with the b phase "fingers" on the back of the breaker.
An electrician bent the stab back up into line with the other two and we were able to rack it back in with no problems. He said it was "single phasing". how does this relate to burned up control transformer and relays?
Is it recommended to inspect other equipment which is powered from this bus.
We had no problems on any of the other 480v busses.
Thanks in advance for your replies.
We had several failures in the circuit breakers on equipment fed from our 5B 480V bus during a startup on our power plant. In one of the breakers a control transformer was burned up, some relays powered from the 5B bus were melted. We found in the circuit breaker from the 5B station service transformer to the 5B 480 Volt bus, the "b" phase "stab" was bent down and was apparently not making good contact with the b phase "fingers" on the back of the breaker.
An electrician bent the stab back up into line with the other two and we were able to rack it back in with no problems. He said it was "single phasing". how does this relate to burned up control transformer and relays?
Is it recommended to inspect other equipment which is powered from this bus.
We had no problems on any of the other 480v busses.
Thanks in advance for your replies.