Single VFD running two 400 HP AC motors driving on-shore oil drill via gears.
One motor is original winding and one was rewound with 10% more copper area and hence 10% lower DC resistance.
Both the motors had the same inductance since the turns are the same.
Upon recommissioning, the rewound motor with lower resistance was running much hotter (60 deg C hotter) than the original one.
Then client VFD team did “ID run that made the motors compatible” whatever that means.
And the 60 deg C temp difference between the motors just vanished.
Can the drive gurus here explain this? Thanks.