Bernoulli31
Mechanical
- Jan 13, 2016
- 51
Good day, everyone!
Question re: secondary containment of a tank.
Code says a containment should be "(vii) capable of containing at least 110 percent of the capacity of the largest tank or manifolded tanks that are connected in such a way as to permit the combined contents to spill, whichever is greater" (NYCRR Part 599).
IFC says: “Secondary Containment for indoor storage areas shall be designed to contain a spill from the largest vessel plus the design flow volume of fire protection water
How should the 110% be interpreted?
In my mind, if the containment "tank" has a volume 11% larger than that of the actual tank, it meets the intent of the Code.
For example:
PRIMARY TANK DIMENSIONS: 30" L X 22" W x 26" H
CONTAINMENT TANK DIMENSIONS: 52" L X 26.5" W x 14" H
Primary tank = 17160 CuIn
Containment = 19292 CuIn
Containment is about 12% larger than primary (>110%)
Does the code allow for the assumption that the volume of the tank that sits within the confines of the containment (to the height of the containment)is to be included in the usable secondary containment volume?
I design aqueducts in a parallel universe.
Question re: secondary containment of a tank.
Code says a containment should be "(vii) capable of containing at least 110 percent of the capacity of the largest tank or manifolded tanks that are connected in such a way as to permit the combined contents to spill, whichever is greater" (NYCRR Part 599).
IFC says: “Secondary Containment for indoor storage areas shall be designed to contain a spill from the largest vessel plus the design flow volume of fire protection water
How should the 110% be interpreted?
In my mind, if the containment "tank" has a volume 11% larger than that of the actual tank, it meets the intent of the Code.
For example:
PRIMARY TANK DIMENSIONS: 30" L X 22" W x 26" H
CONTAINMENT TANK DIMENSIONS: 52" L X 26.5" W x 14" H
Primary tank = 17160 CuIn
Containment = 19292 CuIn
Containment is about 12% larger than primary (>110%)
Does the code allow for the assumption that the volume of the tank that sits within the confines of the containment (to the height of the containment)is to be included in the usable secondary containment volume?